Google Mail Calendar Documents Reader Web more »
Recently Visited Groups | Help | Sign in
Google Groups Home
Earth bonding of machinery
There are currently too many topics in this group that display first. To make this topic appear first, remove this option from another topic.
There was an error processing your request. Please try again.
flag
  13 messages - Collapse all  -  Translate all to Translated (View all originals)
The group you are posting to is a Usenet group. Messages posted to this group will make your email address visible to anyone on the Internet.
Your reply message has not been sent.
Your post was successful
 
From:
To:
Cc:
Follow-up To:
Add Cc | Add Follow-up to | Edit Subject
Subject:
Validation:
For verification purposes please type the characters you see in the picture below or the numbers you hear by clicking the accessibility icon. Listen and type the numbers that you hear
 
robgraham  
View profile   Translate to Translated (View Original)
 More options 7 Nov, 15:48
Newsgroups: uk.d-i-y
From: robgraham <robkgra...@btinternet.com>
Date: Sat, 7 Nov 2009 07:48:32 -0800 (PST)
Local: Sat 7 Nov 2009 15:48
Subject: Earth bonding of machinery
I've recently joined the local wood working club.  Wood turning
instruction is my reason, plus access to somewhat bigger and better
bits of kit than I can afford or have space for.

They just had a new dust extraction system fitted - about half the
size of my workshop!  It's not been wired in.  It's likely to be a
local authority electrican to do it but the club chairman wanted to
know what was likely to be involved.

It set me thinking afterwards about the earth bonding of all the
equipment.  The lathes, for instance, are on 13A plugs, which I don't
think is a good idea, and if they are to be then surely bonding would
be necessary.  If the other equipement is hard wired I take the
bonding is through the power wiring ?

Rob


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
John Rumm  
View profile   Translate to Translated (View Original)
 More options 7 Nov, 18:47
Newsgroups: uk.d-i-y
From: John Rumm <see.my.signat...@nowhere.null>
Date: Sat, 07 Nov 2009 18:47:33 +0000
Local: Sat 7 Nov 2009 18:47
Subject: Re: Earth bonding of machinery

robgraham wrote:
> I've recently joined the local wood working club.  Wood turning
> instruction is my reason, plus access to somewhat bigger and better
> bits of kit than I can afford or have space for.

Sounds like fun...

> They just had a new dust extraction system fitted - about half the
> size of my workshop!  It's not been wired in.  It's likely to be a
> local authority electrican to do it but the club chairman wanted to
> know what was likely to be involved.

> It set me thinking afterwards about the earth bonding of all the

Grrrr, usual comments about the meaninglessness of the phrase "earth
bonding" - no such thing. There is earthing, and there is equipotential
bonding. Different things for different purposes.

> equipment.  The lathes, for instance, are on 13A plugs, which I don't
> think is a good idea, and if they are to be then surely bonding would

Firstly lathes on plugs - not a problem unless they are too large to run
from a 13A supply. There is some argument that the socket circuit ought
to be on a kill switch arrangement in the workshop, but that is a
separate issue.

Secondly, equipotential bonding. A workshop is not a special location or
one of enhanced risk of shock injury, so supplementary bonding is not
required.

(if the lathe were installed in a bathroom or sauna, then EQ bonding
probably would be required[1], as would connection via a FCU rather than
plug and socket, however the CPC in the flex feeding the device would
also double as a bonding conductor and hence a separate one would not be
required)

[1] 17th edition installs with RCD protected everything can skip bonding.

> be necessary.  If the other equipement is hard wired I take the
> bonding is through the power wiring ?

yup.

--
Cheers,

John.

/=================================================================\
|          Internode Ltd -  http://www.internode.co.uk            |
|-----------------------------------------------------------------|
|        John Rumm - john(at)internode(dot)co(dot)uk              |
\=================================================================/


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
James Salisbury  
View profile   Translate to Translated (View Original)
 More options 7 Nov, 19:51
Newsgroups: uk.d-i-y
From: James Salisbury <nntp.dsl.pipex.com>
Date: Sat, 07 Nov 2009 19:51:34 +0000
Local: Sat 7 Nov 2009 19:51
Subject: Re: Earth bonding of machinery

Hang on, if you have metal duct work that you are sending a flammable
dust along you do need to make sure that all metal parts of the duct are
bonded together. Standard 4mm2 should be fine.

With regard to the lathes there should be means of quickly shutting off
the power should a person become entangled in one. One suggested way is
to have a contactor with stop and start buttons feeding all the circuits
in the distribution board and have several E stop buttons round the room.

Dependant on load you could use something like
http://uk.farnell.com/abb-control/312exe1d-ol/starter-dol-15kw-230v/d...

and
http://uk.farnell.com/multicomp/rc1pybs142/22mm-switches-box-em-stop-...

the key is usefully it stops others who are not competent to use a lathe
turning the power on. The prices should be cheaper at an electrical
wholesalers

James


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
robgraham  
View profile   Translate to Translated (View Original)
 More options 7 Nov, 21:30
Newsgroups: uk.d-i-y
From: robgraham <robkgra...@btinternet.com>
Date: Sat, 7 Nov 2009 13:30:16 -0800 (PST)
Local: Sat 7 Nov 2009 21:30
Subject: Re: Earth bonding of machinery
On 7 Nov, 18:47, John Rumm <see.my.signat...@nowhere.null> wrote:

Sorry John - careless typing !

It was the lathes that concerned me most as the end of each session
(twice a day often) the plugs are removed.  I don't know what regime
is in place to inspect the plugs, but such frequent movement could
lead to disconnection of the any of the leads inside the plug, with
the corresponding hazard.  I also do like the concept of central
isolation.

As far as I know everything is covered by and RCD - do you get 3 ph
RCD's ?

Rob


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Dave Osborne  
View profile   Translate to Translated (View Original)
 More options 8 Nov, 00:45
Newsgroups: uk.d-i-y
From: Dave Osborne <DaveyO...@SPAMymail.com>
Date: Sun, 08 Nov 2009 00:45:13 +0000
Local: Sun 8 Nov 2009 00:45
Subject: Re: Earth bonding of machinery

James Salisbury wrote:

> With regard to the lathes there should be means of quickly shutting off
> the power should a person become entangled in one. One suggested way is
> to have a contactor with stop and start buttons feeding all the circuits
> in the distribution board and have several E stop buttons round the room.

Yes, unfortunately, cutting the power to a workshop is not the answer
any more. I've been trying to get to the bottom of this "should there be
a workshop-wide e-stop system" question and I haven't been able to find
any guidance from the HSE, IEE or anybody else to clarify current best
practice. I would welcome any pointers.

The arguments against are that (1) PUWER[1] doesn't require it and (2)
PUWER does require that, even under emergency conditions, work equipment
must be brought to a stop in a controlled manner (particularly where
"[the emergency stop signal would] trigger or permit the triggering of
certain safeguard movements"[2]).

Further, PUWER requires that all guarding and auxiliary circuits (e.g.
task lighting, fume extraction) that enhance safety should remain
functional in the event of an e-stop.

It is usual therefore to consider e-stop on a per-machine basis.

IMO if it were deemed (on the basis of a full risk assessment) that a
workshop-wide e-stop be required, then this e-stop should send an e-stop
signal to each machine rather than cut the power. Depending on detailed
risk-assessment, this could mean modifying the wiring of a machine to
accept an external e-stop signal or fitting a local contactor to cut the
power to an individual machine.

===

[1] Provision and Use of work Equipment Regulations 1998.

http://www.berr.gov.uk/files/file11274.pdf See clauses 1.2.4 and 1.6.3

[2] AIUI (although I can't cite a reference, it may be the EEC machinery
directive) regulations have changed for things like grinding wheels and
table saws. They now must come to a complete standstill within a few
seconds of being turned off (either normal or emergency stop) and with
this being achieved by the provision of d.c. injection braking, simply
cutting power to a machine is not an option under PUWER as the machine
would not then come to a controlled stop, but would run-on for anything
up to several minutes.

===

As an aside, clause 1.5.7 of the above document speaks to the avoidance
of explosion risk being the responsibility of the designer/manufacturer
of the equipment. Therefore, any additional equipotential bonding of a
dust extraction system should only be implemented in accordance with the
manufacturer's requirements.


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
John Rumm  
View profile   Translate to Translated (View Original)
 More options 8 Nov, 03:11
Newsgroups: uk.d-i-y
From: John Rumm <see.my.signat...@nowhere.null>
Date: Sun, 08 Nov 2009 03:11:27 +0000
Local: Sun 8 Nov 2009 03:11
Subject: Re: Earth bonding of machinery

robgraham wrote:
> Sorry John - careless typing !

Not "having a go" really ;-)

> It was the lathes that concerned me most as the end of each session
> (twice a day often) the plugs are removed.  I don't know what regime
> is in place to inspect the plugs, but such frequent movement could

I suppose it should keep the contract surfaces clean... might risk
breaking a flex in time, but twice a day is not a huge amount (compared
to the life of a commercial vacuum cleaner for example).

> lead to disconnection of the any of the leads inside the plug, with
> the corresponding hazard.  I also do like the concept of central
> isolation.

As others have mentioned, that is not always the ideal solution. Much
depends on the type of equipment that is in use. Traditionally there
would be a circuit for which power was supplied via a contactor,  and
stop switches were dotted about to allow the circuit to be de-energised
in an emergency. With more modern machines that use active breaking etc
or require power for safe operation of emergency stop procedures, that
approach is now deprecated, although one might argue that for a small
collection of simple wood lathes it is still a reasonable approach.

Also looking back at the question, I did skip one possible aspect of the
extraction system; that it might have extensive ducting. If this is
metal and snakes from room to room, then it may come under the
definition of extraneous conductive elements that could introduce a
potential into a zone. Hence should to be included in the *main* EQ bonding.

(there is a separate issue with ducting system regarding providing an
earthing path to drain static buildup - where non conductive ducts are
used, a bare earth wire is sometimes routed through the duct to
facilitate this.

> As far as I know everything is covered by and RCD - do you get 3 ph
> RCD's ?

You can yes. Assuming all the equipment is properly earthed, then the
electrocution risks from it will be fairly low anyway.

--
Cheers,

John.

/=================================================================\
|          Internode Ltd -  http://www.internode.co.uk            |
|-----------------------------------------------------------------|
|        John Rumm - john(at)internode(dot)co(dot)uk              |
\=================================================================/


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
PeterC  
View profile   Translate to Translated (View Original)
 More options 8 Nov, 09:42
Newsgroups: uk.d-i-y
From: PeterC <giraffenos....@homecall.co.uk>
Date: Sun, 8 Nov 2009 09:42:19 +0000
Local: Sun 8 Nov 2009 09:42
Subject: Re: Earth bonding of machinery

On Sat, 7 Nov 2009 13:30:16 -0800 (PST), robgraham wrote:
> It was the lathes that concerned me most as the end of each session
> (twice a day often) the plugs are removed.  I don't know what regime
> is in place to inspect the plugs, but such frequent movement could
> lead to disconnection of the any of the leads inside the plug, with
> the corresponding hazard.

We had this at work - the sockets (MK metal-clad) occasionally failed by
falling apart internally sometimes with bang and smoke. Checking sockets
mechanically every few years might be necessary.
Another consideration is the plug: the sort that has a medial split can
fail in a dangerous way, as the operator's fingers can contact the
conductive parts if the sccrew fails, so the fully capped type is better
(the ones that need a bit cutting out to get on after wiring :-)  ).
--
Peter.
The head of a pin will hold more angels if
it's been flattened with an angel-grinder.

    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
James Salisbury  
View profile   Translate to Translated (View Original)
 More options 8 Nov, 09:49
Newsgroups: uk.d-i-y
From: James Salisbury <nntp.dsl.pipex.com>
Date: Sun, 08 Nov 2009 09:49:27 +0000
Local: Sun 8 Nov 2009 09:49
Subject: Re: Earth bonding of machinery

Hi,

You might like to drop a note to these people
http://www.moeller.co.uk/index.htm with full details of all the kit,
they will be able to suggest what is needed.

James


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Andy Dingley  
View profile   Translate to Translated (View Original)
 More options 8 Nov, 10:44
Newsgroups: uk.d-i-y
From: Andy Dingley <ding...@codesmiths.com>
Date: Sun, 8 Nov 2009 02:44:50 -0800 (PST)
Local: Sun 8 Nov 2009 10:44
Subject: Re: Earth bonding of machinery
On 8 Nov, 00:45, Dave Osborne <DaveyO...@SPAMymail.com> wrote:

> Yes, unfortunately, cutting the power to a workshop is not the answer
> any more.

Indeed.

> I've been trying to get to the bottom of this "should there be
> a workshop-wide e-stop system" question

Clearest I've seen has been school's workshop advice, at the LEA
level. Which varies between LEAs.  Where a single e-stop system is
required, it's necessary to integrate it with the e-stop on each
machine (braking etc.), where that's relevant for that machine (which
then gets awkward for some).

It does seem however that schools no longer have anything
interestingly large, so the e-stop braking issue becomes moot.


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Owain  
View profile   Translate to Translated (View Original)
 More options 8 Nov, 12:57
Newsgroups: uk.d-i-y
From: Owain <spuorgelg...@gowanhill.com>
Date: Sun, 8 Nov 2009 04:57:20 -0800 (PST)
Local: Sun 8 Nov 2009 12:57
Subject: Re: Earth bonding of machinery
On 7 Nov, 21:30, robgraham  wrote:

> It was the lathes that concerned me most as the end of each session
> (twice a day often) the plugs are removed.  

There may be a case for having a "teacher's" keyswitch to disable
power to the machinery *separate from emergency stop*.

In a factory anyone using the room should be safety-trained; even if
they don't operate the machinery there should be a safety induction.
In a school or similar facility the workshop may be used for a variety
of purposes or levels of instruction, and although people shouldn't be
in the workshop unsupervised it is probably going to happen at some
point. So the machinery should be locked off when the papercrafting
group are using the room.

Owain


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
robgraham  
View profile   Translate to Translated (View Original)
 More options 8 Nov, 13:01
Newsgroups: uk.d-i-y
From: robgraham <robkgra...@btinternet.com>
Date: Sun, 8 Nov 2009 05:01:24 -0800 (PST)
Local: Sun 8 Nov 2009 13:01
Subject: Re: Earth bonding of machinery
On 8 Nov, 03:11, John Rumm <see.my.signat...@nowhere.null> wrote:

I'll get my grrr! back now - people who say 'breaking' when they mean
'braking' !!  No smileys available so I'll just do [BG].

Anyway it's been an interesting response from you all - thanks.  I'll
raise the points with the club chairman and possibly point him to this
thread.
Rob

Rob


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Dave Osborne  
View profile   Translate to Translated (View Original)
 More options 8 Nov, 13:21
Newsgroups: uk.d-i-y
From: Dave Osborne <DaveyO...@SPAMymail.com>
Date: Sun, 08 Nov 2009 13:21:50 +0000
Local: Sun 8 Nov 2009 13:21
Subject: Re: Earth bonding of machinery

Owain wrote:
> On 7 Nov, 21:30, robgraham  wrote:
>> It was the lathes that concerned me most as the end of each session
>> (twice a day often) the plugs are removed.  

> There may be a case for having a "teacher's" keyswitch to disable
> power to the machinery *separate from emergency stop*.

Or a padlocked isolator?

    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Discussion subject changed to "Industrial plugs Re: Earth bonding of machinery" by alexander.keys1
alexander.keys1  
View profile   Translate to Translated (View Original)
 More options 9 Nov, 21:47
Newsgroups: uk.d-i-y, uk.railway, uk.transport.london
From: "alexander.keys1" <alexander.ke...@googlemail.com>
Date: Mon, 9 Nov 2009 13:47:16 -0800 (PST)
Local: Mon 9 Nov 2009 21:47
Subject: Industrial plugs Re: Earth bonding of machinery
On 8 Nov, 09:42, PeterC <giraffenos....@homecall.co.uk> wrote:

You need to replace the '13 Amp' BS1363 plugs & sockets with
industrial connectors, such as the 'Commando' type, made by many
manufacturers to BS EN 60309-2 (formerly BS 4343). These do vary a bit
in quality, but these two manufacturers seem to offer a quality
product, available in metalclad versions as well as the more common
plastic:

http://www.lewden.net/

http://www.a-belco.co.uk/Connectors/CEEGO.html

or for real class there's the 'Reyrolle' BS196 connectors:

http://www.a-belco.co.uk/Connectors/Easigo.html

as used by the former nationalised industries, BR, CEGB, LT etc.

BS1363 connectors were only really intended for domestic purposes, to
provide sockets which could be mass-produced cheaply for the post-WW2
rebuilding programme, they do not stand up to industrial use. Even
BS546 round-pin connectors are better.

Lewden do make a superior weatherproof version of the above types
though, both the plugs and the sockets, look up the 'Weathertight'
range on their website.


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
End of messages
« Back to Discussions « Newer topic     Older topic »

Create a group - Google Groups - Google Home - Terms of Service - Privacy Policy
©2009 Google