PID autotuning - not working for heating application
There are currently too many topics in this group that display first. To make this topic appear first, remove this option from another topic.
There was an error processing your request. Please try again.
flag
  Messages 1 - 25 of 51 - Collapse all  -  Translate all to Translated (View all originals)   Newer >
The group you are posting to is a Usenet group. Messages posted to this group will make your email address visible to anyone on the Internet.
Your reply message has not been sent.
Your post was successful
 
From:
To:
Cc:
Follow-up To:
Add Cc | Add Follow-up to | Edit Subject
Subject:
Validation:
For verification purposes please type the characters you see in the picture below or the numbers you hear by clicking the accessibility icon. Listen and type the numbers that you hear
 
Frank W.  
View profile   Translate to Translated (View Original)
 More options 5 Nov, 17:37
Newsgroups: comp.arch.embedded
From: "Frank W." <frankw_use...@mailinator.com>
Date: Thu, 5 Nov 2009 18:37:21 +0100
Local: Thurs 5 Nov 2009 17:37
Subject: PID autotuning - not working for heating application
Is there a control engineering expert here?

I could us a bit of help on how to implement a PID autotune function for a
heating application (a small boiler).

My current PID autotune function produces no reliable results. I use the
relay feedback method (Åstrom and Hägglund) but it seems that the ultimate
period Tu - one of the paramters determined with the relay feedback test -
is directly correlated to the relay output step u. u is an arbitrary value
which makes Tu an arbitary value. Since Tu is required to compute Ti and Td
(e.g. Ti = 0.5 Tu = Ziegler-Nichols), autotune is not possible.

I believe this is because the machine heats very quickly (1500W boiler) and
cools down very slowly, so the process value isn't a sinusoid. Here is an
example graphics, green line is setpoint, red plot is process value and the
grey vertical bars represent heat output u:

http://img196.imageshack.us/img196/7409/examplejr.jpg

Regardless of u, the temperature always dips the same, small amount below
setpoint - because the machine cools slowly, the temperature can not fall
far below setpoint before it's reacting to the heat. It then shoots up by an
amount that is proportional to u. As a result, the plot resembles mountains
above setpoint. If u is large, temperature will shoot high above the
setpoint and take very long to cool down. Big mountains, so Tu gets large,
Tu ~ u = my problem.

Since all PID temperature controllers have Autotune, there must be a
solution for this problem. Any ideas?


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Vladimir Vassilevsky  
View profile   Translate to Translated (View Original)
 More options 5 Nov, 19:09
Newsgroups: comp.arch.embedded
From: Vladimir Vassilevsky <nos...@nowhere.com>
Date: Thu, 05 Nov 2009 13:09:43 -0600
Local: Thurs 5 Nov 2009 19:09
Subject: Re: PID autotuning - not working for heating application

Frank W. wrote:
> Is there a control engineering expert here?

You can contact Tim Wescott who is the expert in control systems,
however the problem is not really a rocket science.

> I could us a bit of help on how to implement a PID autotune function for a
> heating application (a small boiler).

It looks like a huge lag in the control loop. PID approach won't work
very well. Is your heater on-off type or proportionally regulated?

> Since all PID temperature controllers have Autotune, there must be a
> solution for this problem. Any ideas?

To begin with, abandon autotune and see if you can get good control by
manual adjustment of parameters.

Vladimir Vassilevsky
DSP and Mixed Signal Design Consultant
http://www.abvolt.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Bob  
View profile   Translate to Translated (View Original)
 More options 5 Nov, 22:43
Newsgroups: comp.arch.embedded
From: Bob <SkiBoy...@excite.com>
Date: Thu, 05 Nov 2009 14:43:57 -0800
Local: Thurs 5 Nov 2009 22:43
Subject: Re: PID autotuning - not working for heating application

As someone else said: try manually adjusting parameters, instead. Do you
really need autotune? If the boiler/heater/load/setpoint don't change
much, then twiddle the parameters until you like the result.

That said, there are at least a dozen algorithms for autotuning. They
fall into two basic methods (relay and step), but the parameters they
generate can be quite different due to the different desired responses
(e.g. "fastest to reach a certain error after a step change in setpoint"
vs "little or no overshoot after a disturbance", etc.). You have to be
clear about what you're trying to do before you bother trying to tune it.

Large delay and overshoot are common to heater control loops. Placing
the sensor as close as possible to the heater can help, but then you
might not be measuring the thing you want hot. I just had a (maybe)
similar problem that included a requirement for a smooth ramp of the
temperature. That led me to close the loop around the slope (calculated
with an extremely simple FIR filter) during ramping. The slope-loop
worked far better than trying get the temperature-loop to follow a
ramping setpoint.

YMMV
Bob


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Tim Wescott  
View profile   Translate to Translated (View Original)
 More options 6 Nov, 05:48
Newsgroups: comp.arch.embedded
From: Tim Wescott <t...@seemywebsite.com>
Date: Thu, 05 Nov 2009 23:48:04 -0600
Local: Fri 6 Nov 2009 05:48
Subject: Re: PID autotuning - not working for heating application

On Thu, 05 Nov 2009 13:09:43 -0600, Vladimir Vassilevsky wrote:
> Frank W. wrote:

>> Is there a control engineering expert here?

> You can contact Tim Wescott who is the expert in control systems,
> however the problem is not really a rocket science.

Or you can wait for him to get around to doing the newsgroup thang.

(thanks for the plug).

I'll bet there's rockets out there with temperature loops.

>> I could us a bit of help on how to implement a PID autotune function
>> for a heating application (a small boiler).

> It looks like a huge lag in the control loop. PID approach won't work
> very well. Is your heater on-off type or proportionally regulated?

>> Since all PID temperature controllers have Autotune, there must be a
>> solution for this problem. Any ideas?

> To begin with, abandon autotune and see if you can get good control by
> manual adjustment of parameters.

Ditto -- try it by hand, and go from there.

--
www.wescottdesign.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Tim Wescott  
View profile   Translate to Translated (View Original)
 More options 6 Nov, 05:55
Newsgroups: comp.arch.embedded
From: Tim Wescott <t...@seemywebsite.com>
Date: Thu, 05 Nov 2009 23:55:05 -0600
Local: Fri 6 Nov 2009 05:55
Subject: Re: PID autotuning - not working for heating application

On Thu, 05 Nov 2009 18:37:21 +0100, Frank W. wrote:
> Is there a control engineering expert here?

> I could us a bit of help on how to implement a PID autotune function for
> a heating application (a small boiler).

> My current PID autotune function produces no reliable results. I use the
> relay feedback method (Åstrom and Hägglund) but it seems that the
> ultimate period Tu - one of the paramters determined with the relay
> feedback test - is directly correlated to the relay output step u. u is
> an arbitrary value which makes Tu an arbitary value. Since Tu is
> required to compute Ti and Td (e.g. Ti = 0.5 Tu = Ziegler-Nichols),
> autotune is not possible.

Are you sure you haven't just stopped too soon in turning the output step
down?  I see where you're having trouble with this; is there some reason
you can't turn u down even further?  Things may start looking better when
you get it down to where the temperature curve is roughly symmetrical
around the average.

Why do you want to use autotune?  If this is a product that you're
working on, and if the boiler design is the same for all of the parts
that you ship, then you should just need one tuning.

Autotune is for when you're selling a shrink-wrapped controller that has
to work for anything -- and autotune is often considered to be a good way
to get the tuning in the ballpark so that a human can get involved and
actually make it work right.

Unless you need to adapt to a variety of different, unexpected boiler
combinations -- that don't change as the boiler is operating -- then
there's not much value in autotune, IMHO.

--
www.wescottdesign.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Frank W.  
View profile   Translate to Translated (View Original)
 More options 6 Nov, 14:15
Newsgroups: comp.arch.embedded
From: "Frank W." <frankw_use...@mailinator.com>
Date: Fri, 6 Nov 2009 15:15:08 +0100
Local: Fri 6 Nov 2009 14:15
Subject: Re: PID autotuning - not working for heating application

"Tim Wescott" <t...@seemywebsite.com> wrote:
> you can't turn u down even further?

A bit. Sensor resolution is the limit. The temperature hardly drops below
the setpoint during relay test iterations because the system cools so slowly
(it drops 0.3 degree below setpoint in case of my machine's 200ml boiler),
so making it nearly symmetric creates a PV signal with very few steps.

>  Things may start looking better when

I didn't say that the results are bad. It's just that I don't know which of
the results to pick since every variation of the relay output step produces
a different ultimate period. The lower u is made, the lower Tu gets (there
is no lower limit).

> Why do you want to use autotune?  If this is a product that you're
> working on, and if the boiler design is the same for all of the parts
> that you ship, then you should just need one tuning.

The algorithm is for a semi-commercial PID controller for coffee machines,
so autotune can not be left out since users expect it. Boiler sizes rougly
vary from 200ml to a few thousand ml. Wattage varies not so much (from
1250W-2500W).

    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Tim Wescott  
View profile   Translate to Translated (View Original)
 More options 7 Nov, 01:17
Newsgroups: comp.arch.embedded
From: Tim Wescott <t...@seemywebsite.com>
Date: Fri, 06 Nov 2009 19:17:15 -0600
Local: Sat 7 Nov 2009 01:17
Subject: Re: PID autotuning - not working for heating application

It sounds like an ideal application for autotune -- you have a wide and
uncontrolled product range, so you can't just make a 'one size fits all'
tuning.  On the other hand your plants are constrained to a certain class
of systems, so your basic problem isn't so wide open as to be impossible.

Any sort of tuning exercise involves making some assumptions about the
system you're controlling, poking it with some excitation, seeing how it
responds, then formulating a controller for the thing.  In some cases you
have a step in there where you create a mathematical model of your plant,
in others you don't.  The process is the same with autotuning, except
that you hope to have a machine doing the tedious bits for you, instead
of you having to run around the world tuning up coffee makers.

The Aostroem-Haggluend method never develops that explicit model, nor
does it work with just any old excitation -- it just pokes the system in
a specific way, extracts some parameters that aren't really closely
related to what control theorists are used to (but which are practically
quite useful), then gets PID tuning parameters from those measured system
parameters.

Your problem is that you're not really poking the system in quite the
right way, so the Aostroem-Haggluend method is breaking down for you.

Clearly there are two ways you can go:  one, poke the system the _right_
way, and two, abandon the A-H method.  You _could_ use excitation and
response with more 'university' style adaptive control methods to derive
a system model and develop a controller -- this is not a bad way to go if
you're comfortable wrangling the math.  Or you can try to fix your
excitation, or you can use the open-loop A-H method of data collection.

Have you tried turning your drive way down and adding some substantial
hysteresis to your relay function?  I.e. instead of the relay being a
static rule that says "output = on if above threshold, output = off if
below", you make the rule say "go from off to on if above a low
threshold, go from on to off if above a high threshold".  Make the two
thresholds far enough apart (5 or 10 degrees?) to insure you capture good
data, then find a value for your drive that seems to give good results
for a variety of boiler sizes.

Or you can use the open-loop A-H -- this is actually the original method
that Ziegler and Nichols used (as far as I know).  In it you start from
steady state, make a step change in the drive, and look for a ramp
response in the output.  You deduce gain and delay from the slope of the
ramp and the delay from that ramp to an ideal 'immediate' ramp.  In your
case you probably want to take off from a fairly hot temperature, so you
may want to get up to your launch temperature with a really, really slow
integrator-only loop or some other means that'll get you at a steady
temperature safely.  Once you're at a constant temperature and drive, you
can step the drive and start collecting data points on the response.

Or hire me :-).

--
www.wescottdesign.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Frank W.  
View profile   Translate to Translated (View Original)
 More options 9 Nov, 07:36
Newsgroups: comp.arch.embedded
From: "Frank W." <frankw_use...@mailinator.com>
Date: Mon, 9 Nov 2009 08:36:52 +0100
Local: Mon 9 Nov 2009 07:36
Subject: Re: PID autotuning - not working for heating application

"Tim Wescott" <t...@seemywebsite.com> wrote:
> you're not really poking the system in quite the right way

Possible. The original method is: if the process value crosses sepoint, the
heat is turned on (below setpoint) or off (above). One has to determine
steady state output (us) first and apply steps to the heating element on
this basis: heat = us +- u. This limits heat output if you want to avoid
getting into saturation: if us = 6%, as it is in my case, then you can not
have larger output steps than 6% (to avoid getting below 0%), ie. power
swings from 0% to 12%. Since that's too low to generate peaks that I can
measure with good resolution, I deviate from the inherent step limit of the
original algorithm and excite the system with larger steps (e.g. 0 - 25% =
+-12.5%). I'm now trying to minimize the possible effect of this deviation
my incrementally reducing u until I have swings that are just big enough to
be measured with resaonable resolution.

> Or you can use the open-loop A-H -- this is actually the original method
> that Ziegler and Nichols used (as far as I know).  In it you start from
> steady state, make a step change in the drive, and look for a ramp
> response in the output.

I don't think this would work any better because this test requires special
osciallations, too. There are very fast PV rises in my system because the
sensor is on the outside of a thick, small die-cast aluminium boiler and
close to strong heating elements. And there are very slow declines, dictated
by the small, natural heat dissipation of a water-filled boiler (no flow).
That means I can't find the special P that creates oscillations because all
do: even a small P will cause forced oscillatations of PV because the system
is dampend so much in one direction.

    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Tim Wescott  
View profile   Translate to Translated (View Original)
 More options 9 Nov, 16:33
Newsgroups: comp.arch.embedded
From: Tim Wescott <t...@seemywebsite.com>
Date: Mon, 09 Nov 2009 10:33:08 -0600
Local: Mon 9 Nov 2009 16:33
Subject: Re: PID autotuning - not working for heating application
On Mon, 09 Nov 2009 08:36:52 +0100, Frank W. wrote:

        <begin restored context>

It sounds like an ideal application for autotune -- you have a wide and
uncontrolled product range, so you can't just make a 'one size fits all'
tuning.  On the other hand your plants are constrained to a certain class
of systems, so your basic problem isn't so wide open as to be impossible.

Any sort of tuning exercise involves making some assumptions about the
system you're controlling, poking it with some excitation, seeing how it
responds, then formulating a controller for the thing.  In some cases you
have a step in there where you create a mathematical model of your plant,
in others you don't.  The process is the same with autotuning, except
that you hope to have a machine doing the tedious bits for you, instead
of you having to run around the world tuning up coffee makers.

The Aostroem-Haggluend method never develops that explicit model, nor
does it work with just any old excitation -- it just pokes the system in
a specific way, extracts some parameters that aren't really closely
related to what control theorists are used to (but which are practically
quite useful), then gets PID tuning parameters from those measured system
parameters.

Your problem is that you're not really poking the system in quite the
right way, so the Aostroem-Haggluend method is breaking down for you.

Clearly there are two ways you can go:  one, poke the system the _right_
way, and two, abandon the A-H method.  You _could_ use excitation and
response with more 'university' style adaptive control methods to derive
a system model and develop a controller -- this is not a bad way to go if
you're comfortable wrangling the math.  Or you can try to fix your
excitation, or you can use the open-loop A-H method of data collection.

Have you tried turning your drive way down and adding some substantial
hysteresis to your relay function?  I.e. instead of the relay being a
static rule that says "output = on if above threshold, output = off if
below", you make the rule say "go from off to on if above a low
threshold, go from on to off if above a high threshold".  Make the two
thresholds far enough apart (5 or 10 degrees?) to insure you capture good
data, then find a value for your drive that seems to give good results
for a variety of boiler sizes.

Or you can use the open-loop A-H -- this is actually the original method
that Ziegler and Nichols used (as far as I know).  In it you start from
steady state, make a step change in the drive, and look for a ramp
response in the output.  You deduce gain and delay from the slope of the
ramp and the delay from that ramp to an ideal 'immediate' ramp.  In your
case you probably want to take off from a fairly hot temperature, so you
may want to get up to your launch temperature with a really, really slow
integrator-only loop or some other means that'll get you at a steady
temperature safely.  Once you're at a constant temperature and drive, you
can step the drive and start collecting data points on the response.
        <end restored context>

I hear an attempt at a logical, 'software engineer's' description of the
behavior of the system.  "First event A happens, which causes event B,
then event C happens, which causes event D, etc.".  This is sensible for
most problems that one solves with embedded code, but it isn't a way that
works for most control loops -- mostly because in a dynamic system like
this, even if the driving force can be separated into discrete events,
the response to the driving force gets spread out all over everything.

I do not believe that your temperature response to heat input is as
nonlinear as you think it is.  This is partially because in my experience
thermal systems themselves are pretty linear (and therefore act the same
in both directions), and partially because looking at your graph I don't
see any true signs of underdamped behavior -- I see a system that is
responding to asymmetrically, yes, but it looks like a linear response to
an asymmetrical input.

To hazard a guess, I'd say that one way or another when you command a 6%
drive to your heater you're getting 1/4 as much heat as when you command
a 12% drive -- almost as if you're commanding a steady voltage to the
heater, or you're commanding the timing on an SCR drive, or something.  
The response that you're getting looks very much like the response you'd
expect with a 3/4 'on' drive, and a -1/4 'off' drive, which is consistent
with an ambient cooling at your set point temperature that's 1/4 as
strong as the heating you get when the thing is on.

If you're really exciting a nonlinearity in the heating system you want
to find it and characterize it now, rather than struggling with
mysterious voodoo code for the rest of your career.

My recommended method would be to do it by analysis, but since you're
already set up for measurements, making a chart of heater commands vs.
final temperature, from 0 up through whatever gets to the maximum water
temperature you can tolerate (I'd go for a gentle simmer, unless that
causes some non-reversible safety mechanism to go off).  If the chart
shows a curved line you have a nonlinearity in your drive that you need
to deal with (otherwise you have a nonlinearity somewhere else).

--
www.wescottdesign.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Frank W.  
View profile   Translate to Translated (View Original)
 More options 9 Nov, 19:32
Newsgroups: comp.arch.embedded
From: "Frank W." <frankw_use...@mailinator.com>
Date: Mon, 9 Nov 2009 20:32:29 +0100
Local: Mon 9 Nov 2009 19:32
Subject: Re: PID autotuning - not working for heating application

"Tim Wescott" <t...@seemywebsite.com> wrote:
> To hazard a guess, I'd say that one way or another when you command a 6%
> drive to your heater you're getting 1/4 as much heat as when you command a
> 12% drive

95C steady state with 7% heat and 80C steady state with 3.5% heat. Heating
from room temperature to 95C takes ~1min, cooling takes hours (cooling from
95C to 80C takes 15min).

Ultimate gain can be computed just fine, it doesn't matter much what output
steps are used during autotuning. The  Åström/Hägglund result is always ~25%
Kc gain and that works fine and seems right; manual tuning suggests a
similiar value.

It was only ultimate period that gave me problems. Different excitations
during autotuning result in different periods. However, after the recent
changes (minimizing excitation with the goal of creating autotuning peaks
that are as small as possible but large enough to exceed sensor resolution,
thus turning the curve more into a sinus), it seems I get fairly consistent
results that work: Td is calcluated as 2.5s. Manual tuning suggests 1.6s.
That's good enough for me, so I consider the case closed. Thanks for your
help, Tim.


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Oliver Betz  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 08:49
Newsgroups: comp.arch.embedded
From: Oliver Betz <ob...@despammed.com>
Date: Tue, 10 Nov 2009 09:49:01 +0100
Local: Tues 10 Nov 2009 08:49
Subject: Re: PID autotuning - not working for heating application

"Frank W." wrote:
>"Tim Wescott" <t...@seemywebsite.com> wrote:

>> To hazard a guess, I'd say that one way or another when you command a 6%
>> drive to your heater you're getting 1/4 as much heat as when you command a
>> 12% drive
>95C steady state with 7% heat and 80C steady state with 3.5% heat. Heating

Did you consider possible long time constants for "steady state"? Slow
warming of enclosures can ruin your model extraction.

And what is "heat", IOW how do you control the heater - phase angle,
full wave? As Tim wrote, there might be a nonlinear function. And if
you control a SCR without mains synchronisation, you might get huge
uncertainties for low power values.

>from room temperature to 95C takes ~1min, cooling takes hours (cooling from
>95C to 80C takes 15min).

1k/min : 70k/min = 1.4%, that's not so far off from 3.5% to assume
nonlinear behaviour. And your cooling experiment might be influenced
by a hot environment.

Oliver
--
Oliver Betz, Munich
despammed.com might be broken, use Reply-To:


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Frank W.  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 09:40
Newsgroups: comp.arch.embedded
From: "Frank W." <frankw_use...@mailinator.com>
Date: Tue, 10 Nov 2009 10:40:10 +0100
Local: Tues 10 Nov 2009 09:40
Subject: Re: PID autotuning - not working for heating application

"Oliver Betz" <ob...@despammed.com> wrote:
> And what is "heat", IOW how do you control the heater - phase angle,
> full wave?

Full wave. Phase angle is not permitted here with so much wattage.

> you control a SCR without mains synchronisation, you might get huge
> uncertainties for low power values.

The relay has a ZC circuit. 50hz power and 1s cycle time means 100 zero
crossings/cycle, ie. 1% granularity, equals 0.5% average error.

    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Datesfat Chicks  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 16:54
Newsgroups: comp.arch.embedded
From: "Datesfat Chicks" <datesfat.chi...@gmail.com>
Date: Tue, 10 Nov 2009 11:54:36 -0500
Local: Tues 10 Nov 2009 16:54
Subject: Re: PID autotuning - not working for heating application
"Frank W." <frankw_use...@mailinator.com> wrote in message

news:7lggquF3dt584U1@mid.dfncis.de...

> Since all PID temperature controllers have Autotune, there must be a
> solution for this problem. Any ideas?

As you probably know from control theory, the basic theory of a PID
controller is that you have a system described by a set of linear
differential equations that is inherently unstable or has some performance
problems.  As a result you strap a PID controller onto it (with said
controller also described by its own linear differential equations), and the
resulting system (now described by linear differential equations which are a
mathematical mix of the underlying system and the PID controller) has better
characteristics.

Did you notice that there is a word that appears many times in my
description above?

Want to guess what the word is?

That word is "linear".

A system with a time delay is not described by linear differential
equations.  Strapping a PID controller onto it is bad math.

One of the more classic examples is a shower or an industrial process that
mixes fluids of varying temperature and the sensor is located substantially
downstream from the mixing value.  This is a pure time delay.  My shower at
home is like that.  I turn the water a little hotter.  Nothing happens.  I
turn it a little more hotter.  Nothing happens.  Then I turn it a little
more hotter.  Then the wave of hot liquid hits me and I scream in agony.

Over time, I've adapted to my shower.  I don't burn myself anymore.

I think the control algorithms you want to use for a system like yours fall
outside the range of PID.  I'm sure there is a body of theory that covers
it, but I don't know what that is.

I would heat the system full bore for a fixed period of time, then stop and
wait to see how the temperature catches up.  And work from there.

The best control strategy for that system isn't going to be PID.  That is a
non-linear system.

Datesfat


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Datesfat Chicks  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 17:00
Newsgroups: comp.arch.embedded
From: "Datesfat Chicks" <datesfat.chi...@gmail.com>
Date: Tue, 10 Nov 2009 12:00:47 -0500
Local: Tues 10 Nov 2009 17:00
Subject: Re: PID autotuning - not working for heating application
"Datesfat Chicks" <datesfat.chi...@gmail.com> wrote in message

news:qZSdncz-fbqoB2TXnZ2dnUVZ_uGdnZ2d@giganews.com...

From Wikipedia's entry on PID controllers:

http://en.wikipedia.org/wiki/PID_controller

<QUOTE>
Another problem faced with PID controllers is that they are linear. Thus,
performance of PID controllers in non-linear systems (such as HVAC systems)
is variable. Often PID controllers are enhanced through methods such as PID
gain scheduling or fuzzy logic. Further practical application issues can
arise from instrumentation connected to the controller. A high enough
sampling rate, measurement precision, and measurement accuracy are required
to achieve adequate control performance.
</QUOTE>

I don't know what the best control strategy is, but it ain't PID.

Datesfat


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Tim Wescott  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 17:54
Newsgroups: comp.arch.embedded, sci.engr.control
From: Tim Wescott <t...@seemywebsite.com>
Date: Tue, 10 Nov 2009 11:54:21 -0600
Local: Tues 10 Nov 2009 17:54
Subject: Re: PID autotuning - not working for heating application

I've been resisting forking this over into the control newsgroup: now
it's compelling.

Systems with delay can be perfectly linear, as well as time invariant --
they just can't be described by ordinary differential equations with a
finite number of states.

To be linear, a system only needs to satisfy the superposition property.  
A delay element satisfies superposition just fine.

And while a PID controller may not be the theoretically best controller
for a system with delay, in many cases it's not a bad choice at all.  PID
controllers can and will give perfectly satisfactory service with plants
that have significant delay.  The thousands, if not millions, of PID
controllers in mills and factories around the world that are controlling
plants whose responses are dominated by delay certainly belie any
declaration that the PID controller isn't a good choice to control a
plant with delay.

None of the above is intended to minimize the difficulty in analyzing and
designing a truly optimal controller for a plant with pure delay --
that's an exercise that can make your brain hurt, and fast.  And nothing
of the above is intended to chase you away from taking plant delays more
directly into account if a discrete-state controller such as a PID won't
let you eke the performance that you need out of your plant.  

But in the absence of significant nonlinearities or time varying behavior
you can use all the analysis tools that are suitable for linear time
invariant systems on a system with delays just fine.  You can do good
design work, without ever having to explicitly write out the differential
equations, much less solving them.

So if you don't want to get lost in Mathemagic Land searching for
performance that isn't necessary for your product's success, a good ol'
PID controller may be exactly the optimal controller -- in terms of
adequate performance and reasonable engineering time -- even if it
doesn't satisfy any egghead academic measure of "optimal" for the
particular plant you're trying to control.

--
www.wescottdesign.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Datesfat Chicks  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 18:24
Newsgroups: comp.arch.embedded, sci.engr.control
From: "Datesfat Chicks" <datesfat.chi...@gmail.com>
Date: Tue, 10 Nov 2009 13:24:00 -0500
Subject: Re: PID autotuning - not working for heating application
"Tim Wescott" <t...@seemywebsite.com> wrote in message

news:rPCdnSIjis5QNWTXnZ2dnUVZ_oli4p2d@web-ster.com...

> Systems with delay can be perfectly linear, as well as time invariant --
> they just can't be described by ordinary differential equations with a
> finite number of states.

Hi Tim,

I might have missed something significant here.

It is my assumption that a system with a pure time delay is inherently
non-linear.

Let's take my shower example with a pure delay in the pipes ...

With no delay, you can just say that

   Temperature(t) = Valve_Position

or perhaps with a little thermal mass thrown in you can say that:

   d Temperature / dt = K * (Valve_Position - Temperature)

where of course I'm assuming that valve position and water temperature are
the same thing.

The first is I think a 0'th order linear differential equation and the
second is a 1st-order LDE.

But how would you linearize a system with a pure time delay, exactly?

The shower example with a pure pipe delay between the shower valve and my
skin is fine.

Thanks, Datesfat


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Jerry Avins  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 20:00
Newsgroups: comp.arch.embedded, sci.engr.control
From: Jerry Avins <j...@ieee.org>
Date: Tue, 10 Nov 2009 15:00:43 -0500
Local: Tues 10 Nov 2009 20:00
Subject: Re: PID autotuning - not working for heating application

Datesfat Chicks wrote:
> "Tim Wescott" <t...@seemywebsite.com> wrote in message
> news:rPCdnSIjis5QNWTXnZ2dnUVZ_oli4p2d@web-ster.com...

>> Systems with delay can be perfectly linear, as well as time invariant
>> -- they just can't be described by ordinary differential equations with a
>> finite number of states.

> Hi Tim,

> I might have missed something significant here.

> It is my assumption that a system with a pure time delay is inherently
> non-linear.

Superposition is sufficient proof of linearity. What comes out of a pipe
(assuming that there is no mixing in transit) is almost a delayed linear
superopsition of what is pushed into it, but it is not linear because it
is not a pure delay. When the input velocity increases because both hot
and cold water are flowing, the delay time decreases. Superposition
doesn't strictly apply because the time to look isn't well defined.

Any delay pushes a servo system toward unstable. That's not a linearity
problem.

> Let's take my shower example with a pure delay in the pipes ...

> With no delay, you can just say that

>   Temperature(t) = Valve_Position

> or perhaps with a little thermal mass thrown in you can say that:

>   d Temperature / dt = K * (Valve_Position - Temperature)

> where of course I'm assuming that valve position and water temperature
> are the same thing.

There's also the time it takes the valve to move.

> The first is I think a 0'th order linear differential equation and the
> second is a 1st-order LDE.

> But how would you linearize a system with a pure time delay, exactly?

It's already linear. Just nasty.

> The shower example with a pure pipe delay between the shower valve and
> my skin is fine.

But, as I wrote above, a pipe is onlt a pure delay as long as the flow
is constant.

Jerry
--
Engineering is the art of making what you want from things you can get.
¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯¯


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
pnachtwey  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 20:45
Newsgroups: comp.arch.embedded
From: pnachtwey <pnacht...@gmail.com>
Date: Tue, 10 Nov 2009 12:45:24 -0800 (PST)
Local: Tues 10 Nov 2009 20:45
Subject: Re: PID autotuning - not working for heating application
On Nov 5, 9:37 am, "Frank W." <frankw_use...@mailinator.com> wrote:
> Is there a control engineering expert here?
Yes.
> Since all PID temperature controllers have Autotune, there must be a
> solution for this problem.

Some auto tuning algorithms are pretty crude and I think some
companies implement the simplest auto tuning algorithms just to say
they have one.  It is a marketing thing.  How are the customers to
know the difference?  If they knew the difference they wouldn't need
the auto tuning.

> Any ideas?

Turn down the gain for one.  It looks like the control output , gray
bar, amplitude is variable and not a simple on/off SSR.
Because the plant responds so quickly to the output I think the PID
update time should be faster but then the lack of resolution
will be a limitation.  Using the derivative gain may be handy to but
again the lack of resolution will be a factor.
A tried and true method is the feed forward. If one know how much
control output is require for every temperature then one can compute
the control output and be with a percent or two without even using the
PID gains.  The PID gains are just used to correct for errors in the
feed forward predictions.
You should be able to get very close with a feed forward and a
proportional gain.  The integrator will simply remove the last bit of
error.

Auto tune works great when the plant matches the model AND the system
is properly excited.  If not then auto tune doesn't work so well.  Are
the water levels in the boiler constant?  If not can the water level
be detected?  Obviously the temperature will rise more slow or not as
fast if the boiler is full of water as opposed to being empty.

Does the tuning need to be better for a coffee machine?  Manual tuning
should be easy enough.

When I get serious I prefer to make a model of the system.  The
excitation requires a few steps in the control output.  The steps
should be big enough so the response is clearly more significant than
the noise.  The dead time should be clearly visible and the same goes
for the rise time. One can often get the plant gain, time constant and
dead time by inspection.  If not then one must log the control output
and the response.  Then one fits a FOPDT or SOPDT model to your coffee
machine.  I do this using Scilab's optim or lsqrsolve.  Then one goes
to the www.controlguru.com site and uses the IMC, internal model
control, equations there for computing the gains.  For a FOPDT
Kc=t1/((tc+dt)*K)
ti=t1
Where:
Kc is the controller gain.  It should have units of %output per
degree.
ti is the integrator time constant which is usually in minutes.
t1 is the plant time constant
dt is the dead time
K is the plant gain.  This has units of degree per % control output.
tc is the closed loop time constant.  tc is made smaller for more
aggressive tuning and longer for more conservative tuning.  The value
for tc is dependent on the plant time constant and dead time.  The
formula for tc on on the www.controlguru.com site.

You can see from the equation that the dead time reduces the gain.
Also, if the plant gain changes due to the water level then K will be
a function of water and the controller gain will then be modified as a
function of water level.
Kc=t1/((tc+dt)*K(WaterLevel))

I would start here.  Once the plant gain, time constant and dead time
are know there are other options.  On the www.controlguru.com site
there are formulas for adding the derivative time constant td.   One
can also implement a Smith Predictor.   A Smith Predictor isn't that
hard to implement.  The hard part is finding the plant parameters.

I talked to someone else on the phone about making a high end coffee
or espresso machine a few months back.  Our product was gross overkill
but would have made a nice research tool.

Peter Nachtwey


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Tim Wescott  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 22:52
Newsgroups: comp.arch.embedded, sci.engr.control
From: Tim Wescott <t...@seemywebsite.com>
Date: Tue, 10 Nov 2009 16:52:57 -0600
Local: Tues 10 Nov 2009 22:52
Subject: Re: PID autotuning - not working for heating application

Well, if it's already linear you don't linearize it.

Take the system y = h(x, t) ==> y(t) = x(t - td).  Testing this with
superposition we get

y1(t) = x1(t - td),
y2(t) = x2(t - td),

y1(t) + y2(t) = x1(t - td) + x2(t - td)

which is both h(x1, t) + h(x2, t) and h(x1 + x2, t) -- therefore the
system is linear.

Note that as Jerry points out a shower isn't necessarily a linear system,
unless your shower valve insures a constant flow and the pipes don't have
any turbulence.  Let a vastly simplified version be

y(t) = x(t - kd * x(t)),

(this doesn't capture the delay behavior in even a perfect pipe)

Then we try superposition:

y1(t) = x1(t - kd * x1(t)),
y2(t) = x2(t - kd * x2(t)).

This does _not_ equal the system output to the sum:

ys(t) = x1(t - kd * (x1(t) + x2(t))) + x2(t - kd * (x1(t) + x2(t))).

so this system isn't linear -- but not for the reason that you thought.

--
www.wescottdesign.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Tim Wescott  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 22:59
Newsgroups: comp.arch.embedded
From: Tim Wescott <t...@seemywebsite.com>
Date: Tue, 10 Nov 2009 16:59:27 -0600
Local: Tues 10 Nov 2009 22:59
Subject: Re: PID autotuning - not working for heating application

On Tue, 10 Nov 2009 12:45:24 -0800, pnachtwey wrote:
> On Nov 5, 9:37 am, "Frank W." <frankw_use...@mailinator.com> wrote:
>> Is there a control engineering expert here?
> Yes.
>> Since all PID temperature controllers have Autotune, there must be a
>> solution for this problem.
> Some auto tuning algorithms are pretty crude and I think some companies
> implement the simplest auto tuning algorithms just to say they have one.
>  It is a marketing thing.  How are the customers to know the difference?
>  If they knew the difference they wouldn't need the auto tuning.

-- snip --

> Auto tune works great when the plant matches the model AND the system is
> properly excited.  If not then auto tune doesn't work so well.  Are the
> water levels in the boiler constant?  If not can the water level be
> detected?  Obviously the temperature will rise more slow or not as fast
> if the boiler is full of water as opposed to being empty.

> Does the tuning need to be better for a coffee machine?  Manual tuning
> should be easy enough.

-- snip --

> I talked to someone else on the phone about making a high end coffee or
> espresso machine a few months back.  Our product was gross overkill but
> would have made a nice research tool.

> Peter Nachtwey

Speaking of overkill, why not just use an on-off thermostat with some
hysteresis?  Energy consumption?  Lack of cool?

For that matter, how about modeling the whole range of coffeemakers that
you expect (or that you're willing to warrant the device as working).  
Then see if you can get reasonable performance with just one tuning
setting*.  Then instead of telling the customer he can mess around with
autotune, you can tell him he can just plug & play.

* I've done this on blood pressure monitor; we expected to need four
different tunings for the whole range of cuffs from 'premie arm' to 'fat
guy thigh', and ended up needing just one.

--
www.wescottdesign.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
pnachtwey  
View profile   Translate to Translated (View Original)
 More options 10 Nov, 23:51
Newsgroups: comp.arch.embedded
From: pnachtwey <pnacht...@gmail.com>
Date: Tue, 10 Nov 2009 15:51:33 -0800 (PST)
Local: Tues 10 Nov 2009 23:51
Subject: Re: PID autotuning - not working for heating application
On Nov 10, 2:59 pm, Tim Wescott <t...@seemywebsite.com> wrote:
> Speaking of overkill, why not just use an on-off thermostat with some
> hysteresis?

Good idea, then there are no gains to tweak so coffee can be made
right away and the coffee drinking can begin. How accurate must the
temperature control be on a coffee maker and who would be able to tell
the difference between 85 and 86 degrees C? 85-86 degrees seems to be
a few degrees too low unless Frank W knows something the rest of the
world doesn't.

Peter Nachtwey


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Frank W.  
View profile   Translate to Translated (View Original)
 More options 11 Nov, 08:54
Newsgroups: comp.arch.embedded
From: "Frank W." <frankw_use...@mailinator.com>
Date: Wed, 11 Nov 2009 09:54:22 +0100
Local: Wed 11 Nov 2009 08:54
Subject: Re: PID autotuning - not working for heating application

pnachtwey" <pnacht...@gmail.com> wrote:
> unless Frank W knows something the rest of the world doesn't

Don't speak for the rest of the world if you are an ignoramus.

- With a thermostat, temperature swings are far more pronounced than you
claim. It's not just two degrees: The PID has reduced temperature swings of
~15 degree Celsius with the original thermostat to nearly nothing. Such
variations had a noticeable influence on taste (cold = sour). Here's a
PID-vs-thermostat temperature plot for a different, slightly higher-end 500$
home coffee machine which has even bigger 23.9C swings:
http://www.espressoparts.com/espressoparts/content/graphics/pagebuild...
- An equally important benefit is that with a PID instead of a thermostat,
the PV is adjustable. Different beans/roasts call for different brew
temperature - roughly between 85 and 99 degree Celsius.


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
RockyG  
View profile   Translate to Translated (View Original)
 More options 11 Nov, 09:51
Newsgroups: comp.arch.embedded
From: "RockyG" <RobertG...@gmail.com>
Date: Wed, 11 Nov 2009 03:51:50 -0600
Local: Wed 11 Nov 2009 09:51
Subject: Re: PID autotuning - not working for heating application
> Here's a
>PID-vs-thermostat temperature plot for a different, slightly higher-end
500$
>home coffee machine which has even bigger 23.9C swings:
>http://www.espressoparts.com/espressoparts/content/graphics/pagebuild...
>- An equally important benefit is that with a PID instead of a
thermostat,
>the PV is adjustable. Different beans/roasts call for different brew
>temperature - roughly between 85 and 99 degree Celsius

Just for interest, is the boiler pressurised? I saw that the graph show
temepratures higher than 100 deg C. and wondered how they were achieved.          

---------------------------------------        
This message was sent using the comp.arch.embedded web interface on
http://www.EmbeddedRelated.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
pnachtwey  
View profile   Translate to Translated (View Original)
 More options 11 Nov, 15:33
Newsgroups: comp.arch.embedded
From: pnachtwey <pnacht...@gmail.com>
Date: Wed, 11 Nov 2009 07:33:43 -0800 (PST)
Local: Wed 11 Nov 2009 15:33
Subject: Re: PID autotuning - not working for heating application
On Nov 11, 12:54 am, "Frank W." <frankw_use...@mailinator.com> wrote:
> pnachtwey" <pnacht...@gmail.com> wrote:
> > unless Frank W knows something the rest of the world doesn't

> Don't speak for the rest of the world if you are an ignoramus.

You have pissed me off. I searched the internet, the rest of the
world, to find the correct brewing temperature and normal limits which
apparently you don't know and know one else has bothered to do. DON'T
YOU THINK THAT IS IMPORTANT????
I see have wasted my time.

Peter Nachtwey


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Tim Wescott  
View profile   Translate to Translated (View Original)
 More options 11 Nov, 16:35
Newsgroups: comp.arch.embedded
From: Tim Wescott <t...@seemywebsite.com>
Date: Wed, 11 Nov 2009 10:35:13 -0600
Local: Wed 11 Nov 2009 16:35
Subject: Re: PID autotuning - not working for heating application

On Wed, 11 Nov 2009 09:54:22 +0100, Frank W. wrote:
> pnachtwey" <pnacht...@gmail.com> wrote:

>> unless Frank W knows something the rest of the world doesn't

> Don't speak for the rest of the world if you are an ignoramus.

Actually Peter is one of those "control experts" that you were looking
for.  If anything he can claim more pertinent experience at this stuff
than me -- and if a potential customer came to me with a problem that
seemed to be in his bailiwick I wouldn't hesitate* to send them his way.

Control problems seem to attract overly complicated solutions; so one of
the things a responsible control engineer always needs to do is to ask
"is there some bone-head simple way to do this that will be adequate".

> - With a thermostat, temperature swings are far more pronounced than you
> claim. It's not just two degrees: The PID has reduced temperature swings
> of ~15 degree Celsius with the original thermostat to nearly nothing.
> Such variations had a noticeable influence on taste (cold = sour).
> Here's a PID-vs-thermostat temperature plot for a different, slightly
> higher-end 500$ home coffee machine which has even bigger 23.9C swings:
> http://www.espressoparts.com/espressoparts/content/graphics/pagebuilder/

pidsd3c_silvia_tempplot.jpg

> - An equally important benefit is that with a PID instead of a
> thermostat, the PV is adjustable. Different beans/roasts call for
> different brew temperature - roughly between 85 and 99 degree Celsius.

Not to say that you aren't right in the end, but there are thermostats
and there are thermostats.  Design your software for relay control, keep
the hysteresis low and the setpoint adjustable, and you may find that a
swing of a degree or two is quite achievable.  I don't know if it would
be adequate, but you can do a heck of a lot better than a $0.1 snap-
action bit of bimetal and a switch.

Of course, if "PID control" has become a sales point, then you'd better
have it in there.

* I may do so wistfully if work were slow, but I'd still do it.

--
www.wescottdesign.com


    Reply    Reply to author    Forward  
You must Sign in before you can post messages.
To post a message, you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Messages 1 - 25 of 51   Newer >
« Back to Discussions « Newer topic     Older topic »

Create a group - Google Groups - Google Home - Terms of Service - Privacy Policy
©2009 Google