Grounding wire from panel to gas pipe???
Path: g2news2.google.com!news3.google.com!border1.nntp.dca.giganews.com!nntp.giganews.com!nx01.iad01.newshosting.com!newshosting.com!208.49.83.146.MISMATCH!atl-c08.usenetserver.com!news.usenetserver.com!pc03.usenetserver.com!DIALUPUSA.NET!not-for-mail
Date: Wed, 09 Aug 2006 00:44:46 -0500
From: Bud-- <remove.BudN...@isp.com>
User-Agent: Mozilla/5.0 (Windows; U; Win98; en-US; rv:1.7.2) Gecko/20040804 Netscape/7.2 (ax)
X-Accept-Language: en-us, en
MIME-Version: 1.0
Newsgroups: alt.home.repair
Subject: Re: Grounding wire from panel to gas pipe???
References: <u3bchwwob.fsf@nospam.com> <1154371066.634924.133760@75g2000cwc.googlegroups.com> <QVszg.4$9T3.1@newssvr25.news.prodigy.net> <slrnecsrbf.jqk.aznomad@ip70-176-155-130.ph.ph.cox.net> <Ggwzg.34$kO3.19@newssvr12.news.prodigy.com> <d1e97$44d4ba17$4213eb55$24465@DIALUPUSA.NET> <813Bg.2583$9T3.229@newssvr25.news.prodigy.net> <aa45$44d59bfc$4213ea8c$30238@DIALUPUSA.NET> <KllBg.1326$%j7.1059@newssvr29.news.prodigy.net> <22cab$44d6791d$4213ea37$9306@DIALUPUSA.NET> <h8FBg.4651$9T3.2256@newssvr25.news.prodigy.net> <9f66a$44d7667d$4213ea86$15417@DIALUPUSA.NET> <44MBg.2375$%j7.14@newssvr29.news.prodigy.net>
In-Reply-To: <44MBg.2375$%j7.14@newssvr29.news.prodigy.net>
Content-Type: text/plain; charset=windows-1252; format=flowed
Content-Transfer-Encoding: 8bit
Message-ID: <d900a$44d971d4$4213eb17$715@DIALUPUSA.NET>
X-Complaints-To: abuse@usenetserver.com
Organization: UseNetServer.com
Lines: 66
X-Trace: d900a44d971d4e7b64eb200715
Doug Miller wrote:
> In article <9f66a$44d7667d$4213ea86$15...@DIALUPUSA.NET>, Bud-- <remove.BudN...@isp.com> wrote:
>
>>Doug Miller wrote:
>>
>>
>>>In article <22cab$44d6791d$4213ea37$9...@DIALUPUSA.NET>, Bud--
>>
>><remove.BudN...@isp.com> wrote:
>>
>>>>Assume underground metal water service pipe (10ft...) and a ground rod.
>>>>
>>>>Your original statement was:
>>>>
>>>>
>>>>
>>>>>Metal water piping is bonded to the electrical system grounding
>>>>>electrodes to ensure that the metal water piping cannot become live,
>>>>>*not* to provide a ground for the electrical system
>>>
>>>
>>>Yep. And that's correct.
>>>
>>>The water pipe -- by itself -- is not permitted by Code to be used to ground
>>>the electrical system, and hasn't been for many years.
>>>
>>
>>2005 NEC 250.50 "All grounding electrodes as described in 250.52(A)(1)
>>through (A)(6) shall be bonded together to to form the grounding
>>electrode system."
>>
>>250.52(A)(1) "Metal Underground Water Pipe. A metal underground water
>>pipe indirect contact with the earth for 3.0 m (10 ft) or more...."
>>
>>100(1) [definitions] "Grounding Electrode. A device that establishes an
>>electrical connection to the earth."
>>
>>If you are having trouble intrepreting: All grounding electrodes
>>including Metal Underground Water Pipe shall be bonded together to to
>>form the grounding electrode system that establishes an electrical
>>connection to the earth.
>>
>>What do you think it means?
>>
>>Can you read?
>
>
> You're the one who has trouble reading, not me. I never said that metal water
> pipes shouldn't be part of the grounding electrode system -- I said that metal
> water pipes are not permitted to be the *only* grounding electrode, and that's
> a fact.
>
Your fact is not consistent with what you said:
“The electrical system has its own, *separate* grounding electrode.
Metal water piping is bonded to the electrical system grounding
electrodes to ensure that the metal water piping cannot become live,
*not* to provide a ground for the electrical system.”
I do not see how "*not* to provide a ground for the electrical system"
can be read other than the water pipe is not to be a grounding electrode
and the system grounding is provided by the system's "own, *separate*
grounding electrode."
bud--